 Post subject: EXISTING WIRING
PostPosted: Wed Aug 16, 2006 1:17 pm 

Joined: Wed Aug 16, 2006 1:09 pm
Posts: 1
I have a 50 AMP breaker at main panel. I am currently installing a local 50 AMP GFCI control box 5 feet from the spa. The 80 foot run of existing wiring from the main panel directly to the spa is 2 hot black #6 AWG, 1 white #10 AWG and 1 green ground #10 AWG in 3/4 inch gray PVC conduit. Are these wiring sizes correct or should they all be the same gauge? Can the wiring from the local box to the spa control box be the same size as what is coming from the main?


Offline
 Profile  
 
 Post subject:
PostPosted: Wed Aug 16, 2006 5:24 pm 

Joined: Fri Sep 03, 2004 12:27 am
Posts: 1153
Location: Albert Lea, MN
Your hots and neutral need to be the same size, the ground can be one size smaller. I.e. if you use 6 ga hots, use 6 ga neutral, and 8 ga ground. Your conduit is too small for such wires as well.



_________________
Please be patient for replies

ATTENTION! USE THE ADVISE ON THIS FORUM WISELY! WE ARE NOT LIABLE FOR INJURIES, DEATH, DAMAGE, ETC. ARISING FROM THE USE OF THE INFORMATION IN THIS FORUM!

NOTE: I can't guarentee knowledge of all spas.
Offline
 Profile E-mail  
 
Display posts from previous:  Sort by  
 Page 1 of 1 [ 2 posts ] 

All times are UTC - 5 hours


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
AeroBlue: John Olson
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group