 Post subject: # 6 or # 4 gauge for long run of wire
PostPosted: Sun Oct 02, 2005 7:30 pm 

Joined: Mon Sep 19, 2005 9:44 pm
Posts: 2
My 200 amp panel is about 100 feet away from the connection to the tub. I was planning to run 6 x 3 wire using a 60 amp breaker and take that to a 60 amp GFCI about 25 feet from the tub. Given the length of wire run should I be going up to a # 4 wire to avoid voltage drop?

I am planning on refurbishing an older tub with a 240 volt heater and 120 volt pump.


Offline
 Profile  
 
 Post subject:
PostPosted: Wed Oct 12, 2005 1:11 pm 

Joined: Fri Sep 03, 2004 12:27 am
Posts: 1153
Location: Albert Lea, MN
voltage drops aren't a concern on runs under 100 feet. The additonal 25 feet would be minimal, maybe a half a volt. Don't worry about running the 4ga wire. use 6ga



_________________
Please be patient for replies

ATTENTION! USE THE ADVISE ON THIS FORUM WISELY! WE ARE NOT LIABLE FOR INJURIES, DEATH, DAMAGE, ETC. ARISING FROM THE USE OF THE INFORMATION IN THIS FORUM!

NOTE: I can't guarentee knowledge of all spas.
Offline
 Profile E-mail  
 
Display posts from previous:  Sort by  
 Page 1 of 1 [ 2 posts ] 

All times are UTC - 5 hours


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
AeroBlue: John Olson
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group