 Post subject: Ground and Neutral wire size
PostPosted: Tue Mar 27, 2007 1:31 am 

Joined: Mon Mar 26, 2007 10:37 am
Posts: 4
Hooking up 4-wire 240 volt system. Tub is 10 feet from GFI disconnect. Do the ground and neutral wire have to be as large as the hot wires (6 guage)?


Offline
 Profile  
 
 Post subject:
PostPosted: Tue Mar 27, 2007 4:03 pm 
Site Admin
User avatar

Joined: Tue Feb 03, 2004 11:39 am
Posts: 1409
Location: Metro Atlanta, Georgia Region
Some codes may require it, but realistically no.

Most larger spas with 230 volt everything usually have a neutral current draw of no more than 1 amp or so, negating the need for a monster neutral lead.

Ground wires on the other hand, are normally sized according to breaker requirements, not load requirements, which in effect reduces the size of the ground conductor significantly.

Call up a local electrician and see what they say about it...



_________________
Use this information at your own risk!
http://spapartsnet.com
http://atlanta.spanet.net
Amateurs built the Ark, Professionals built the Titanic.
Offline
 Profile E-mail  
 
 Post subject:
PostPosted: Tue Mar 27, 2007 7:03 pm 

Joined: Mon Mar 26, 2007 10:37 am
Posts: 4
Thanks for the input. I really appreciate the useful (and free) info on this site.


Offline
 Profile  
 
Display posts from previous:  Sort by  
 Page 1 of 1 [ 3 posts ] 

All times are UTC - 5 hours


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
AeroBlue: John Olson
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group