 Post subject: Hot springs spa wiring -- no neutral wire on a gfci circuit??
PostPosted: Mon Nov 07, 2005 12:21 am 

Joined: Mon Nov 07, 2005 12:18 am
Posts: 2
Hello,

We just purchased a used hot springs high life (approx 10 years old). The seller did not want to part with the sub-panel in their installation so I am installing a new sub-panel using hot springs' instructions.

I am confused about the GFCI breakers and what I view as an inconistency in the hot springs literature, though, and am looking for some help before I fire the spa up. Here goes:

- The manual states that there are to be two separate 240V circuits servicing the tub. One 20A, and one 30A. Each is supposed to be done with a GFCI breaker

- A common 6GA ground from the subpanel goes to the spa

- The 20A circuit includes hot/hot/neutral -- no problems here, the neutral goes to the gfci breaker, and then the breaker's dedicated neutral to the subpanel neutral bar

- The 30A circuit, however, is supposed to be wired up with hot/hot -- NO NEUTRAL. I cannot understand this; it seems to me that in this setup GFCI would instantly trip... no neutral is wired, and therefore there is a current difference.

Is the above correct? If so do I really need a GFCI breaker on the 30A circuit? If so how should its neutral 'load' terminal be wired (just left floating?).

I've also put in a question to the hot springs folks but am hoping to get a few educated opinions.

Thanks very much!


Offline
 Profile  
 
 Post subject:
PostPosted: Mon Nov 07, 2005 4:11 am 

Joined: Fri Sep 03, 2004 12:27 am
Posts: 1153
Location: Albert Lea, MN
the 30A breaker is for your heater, and yes, it does not get a neutral. Just the two hots. The gfi will sense any current leakage from either of the two hots to ground, and will trip appropriately



_________________
Please be patient for replies

ATTENTION! USE THE ADVISE ON THIS FORUM WISELY! WE ARE NOT LIABLE FOR INJURIES, DEATH, DAMAGE, ETC. ARISING FROM THE USE OF THE INFORMATION IN THIS FORUM!

NOTE: I can't guarentee knowledge of all spas.
Offline
 Profile E-mail  
 
 Post subject:
PostPosted: Mon Nov 07, 2005 9:52 am 

Joined: Mon Nov 07, 2005 12:18 am
Posts: 2
charger_1 wrote:
the 30A breaker is for your heater, and yes, it does not get a neutral. Just the two hots. The gfi will sense any current leakage from either of the two hots to ground, and will trip appropriately


Thank you. One more question: should I connect the neutral pigtail that is included with the gfi breaker on this 30A heater circuit to the neutral bus bar, since there is no 'load' neutral attached?


Offline
 Profile  
 
 Post subject:
PostPosted: Mon Nov 07, 2005 4:11 pm 

Joined: Fri Sep 03, 2004 12:27 am
Posts: 1153
Location: Albert Lea, MN
Quote:
Thank you. One more question: should I connect the neutral pigtail that is included with the gfi breaker on this 30A heater circuit to the neutral bus bar, since there is no 'load' neutral attached?


yes



_________________
Please be patient for replies

ATTENTION! USE THE ADVISE ON THIS FORUM WISELY! WE ARE NOT LIABLE FOR INJURIES, DEATH, DAMAGE, ETC. ARISING FROM THE USE OF THE INFORMATION IN THIS FORUM!

NOTE: I can't guarentee knowledge of all spas.
Offline
 Profile E-mail  
 
Display posts from previous:  Sort by  
 Page 1 of 1 [ 4 posts ] 

All times are UTC - 5 hours


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
cron
AeroBlue: John Olson
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group