I just purchased a new spa and have a couple of questions on running the electrical service to it. It requires a 60 disconnect, I don't have room in my main breaker panel for a 60 amp breaker, can I run the wires from the main busses in the panel to a subpanel located near the spa, approximately 8 feet from the spa and 50 feet from the main panel. Will #6 wire be sufficient for this run?


  
 
 Post subject:
PostPosted: Fri Apr 16, 2004 6:42 pm 
Site Admin
User avatar

Joined: Tue Feb 03, 2004 11:39 am
Posts: 1409
Location: Metro Atlanta, Georgia Region
What you're talking about is NOT a safe (or prudent or legal) thing to do. If you have no room in your box for an extra double pole breaker, there are basically two options:

1. Remove FOUR of the 15 amp standard service breakers, (sitting side by side) and install TWO DOUBLE 15 amp standard service breakers in their place. This will give you two breakers with TWO separate circuits on each. (They'll be the same size as the present ones, only each breaker will have two small switches on them instead of one). Something similar to this: Dual Circuit Breaker

This way, you'll free up two side by side slots for a large main breaker running to the spa.

2. Call an electrician and get an estimate for a break out for a sub-panel.

I would never attempt to bypass the normal legal and practical methods offered by standard breaker options that will work properly in a panel system. Going directly to your mains (in the main box) is not only illegal, it is dangerous, particularly in the long term.

Hope this helps. I've used option number 1 quite a few times and it works well. Just be sure you ascertain the correct brand and type of circuit breaker that your panel requires prior to making the trip off to the supply store -- (take one with you!).

Lastly, I'm trying to figure out what spa requires a sixty amp circuit? If it really does draw sixty amps, then you're pushing it a bit with six gauge wire, especially of this length. I would consider having a pro do it the right way if this is the case.

Thanks.



_________________
Use this information at your own risk!
http://spapartsnet.com
http://atlanta.spanet.net
Amateurs built the Ark, Professionals built the Titanic.
Offline
 Profile E-mail  
 
 Post subject:
PostPosted: Fri Apr 16, 2004 7:14 pm 
Thanks for the information. I thought this was going to be the option. The main panel is fairly new and has 20 spaces, however 12 are already taken up by 220V breakers, AC, Heat, Seperate Shed, Hot Water, dryer and range. I already have a couple of the narrower breakers and was looking for another route. The sap is a VitaSpa model Joli which they say needs a 60 Amp service.

Thanks


  
 
Display posts from previous:  Sort by  
 Page 1 of 1 [ 3 posts ] 

All times are UTC - 5 hours


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
AeroBlue: John Olson
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group