 Post subject: wire question
PostPosted: Wed Nov 01, 2006 7:21 am 

Joined: Tue Oct 31, 2006 7:10 pm
Posts: 2
OK here is what I would like to do.

•From Main electric box in basement run UF 6/3 W G wire from a 240 volt 50 amp circuit breaker (non- GFIC) to the outside wall, about 12 feet.

•Go through wall into PVC conduit which will be located under the deck, attached to the joist, the run is about 12 additional feet.

•Conduit will go to a SPA disconnect panel, located on the deck railing, that has 240 volt 50 Amp GFCI protection. Note this is a 240 50 amp GFCI, not a GFCI circuit Breaker (see this web site: http://www.spadepot.com/Merchant2/merch ... ode=BX8001 to view this disconnect panel)

•The SPA Disconnect Panel is located 6 feet from the spa.

•From the SPA Disconnect Panel I will run 4 separate (3 plus ground) #6 THHN wires in conduit to the spa.

I want to use UF cable so that I do not have to run conduit in the basement (pain in the neck). Is this allowable. I have seen different info on the web ranging from the ground not being insulated in UF Cable so it is not allowable to it is not allowable to have UF cable in conduit for a whole outside run.

Spa Requirements 220 volt 50 amp dedicated circuit, number 6 3 wire with ground, Use THHN copper wire only


Any advice? Thanks


Offline
 Profile E-mail  
 
 Post subject:
PostPosted: Thu Nov 02, 2006 6:22 pm 

Joined: Fri Sep 03, 2004 12:27 am
Posts: 1153
Location: Albert Lea, MN
The wiring should be ok, however I cringe at that type of spa disconnect. It isn't a true fully GFI protected circuit. What it does is uses a small 120V GFI breaker to operate a contactor in the panel. The theory is that if there is a ground fault, it will trip the small breaker, releasing the contactor, thus disconnecting the whole spa. In reality, there can be an instance where the contactor gets welded in the CLOSED position, from arcing, and no matter what that little GFI breaker wants to do, the spa is being fed full power. So, situation is this: Heater shorts out, contacter welds since a shorted heater draws infinite amps (enough to weld), heater opens to the water, GFI breaker senses this and tripps, but low and behold, the heater is still feeding deadly current into the spa, giving the occupants one heck of a ride.



_________________
Please be patient for replies

ATTENTION! USE THE ADVISE ON THIS FORUM WISELY! WE ARE NOT LIABLE FOR INJURIES, DEATH, DAMAGE, ETC. ARISING FROM THE USE OF THE INFORMATION IN THIS FORUM!

NOTE: I can't guarentee knowledge of all spas.
Offline
 Profile E-mail  
 
 Post subject:
PostPosted: Thu Nov 02, 2006 8:08 pm 

Joined: Tue Oct 31, 2006 7:10 pm
Posts: 2
Thanks Charger 1. I appriciate your time and input. What is interesting to me that in my research on the web and in speaking to electricians I get different answers to the same questions. Some love the GFCI SPA disconnect and hate the GFCI Breaker and others are the other way. Same with the wire set-up. Makes it hard to know what to do. Thanks again.


Offline
 Profile E-mail  
 
 Post subject:
PostPosted: Thu Nov 02, 2006 9:00 pm 

Joined: Fri Sep 03, 2004 12:27 am
Posts: 1153
Location: Albert Lea, MN
Personally, I would rather rely on a single device, rather than the 3 required in your applicaton. If any one fail, the whole system can be left unprotected. With a single GFI breaker, they generally fail in a protected state, as long as it is a QUALITY breaker (spit on cutler-hammer here)



_________________
Please be patient for replies

ATTENTION! USE THE ADVISE ON THIS FORUM WISELY! WE ARE NOT LIABLE FOR INJURIES, DEATH, DAMAGE, ETC. ARISING FROM THE USE OF THE INFORMATION IN THIS FORUM!

NOTE: I can't guarentee knowledge of all spas.
Offline
 Profile E-mail  
 
Display posts from previous:  Sort by  
 Page 1 of 1 [ 4 posts ] 

All times are UTC - 5 hours


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
AeroBlue: John Olson
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group