 Post subject: Cal Spa reset GFCI on Heat
PostPosted: Sun Feb 04, 2007 1:34 pm 

Joined: Sun Feb 04, 2007 1:23 pm
Posts: 11
I just installed a '95 Cal Spa Deluxe Model CP-12N. We have it wired with a 50amp breakers at our house electrical panel, going with 6gauge 6/3 wire to a 60amp non fused disconnect 10 ft. from tub, then wiring to the tub. The tub has an internal GFCI breaker built in.

I started it up for the first time last night, watched it warm the water up for a couple hours then headed off to bed. This morning got up to check it and the GFCI had been reset. The water was approx 85* I reset the GFCI and it ran for about 10 minutes before flipping again. I then played with the settings and came up with this: Whenever the heater turns on the GFCI Flips.

These are the diagnostics I have ran:
Check all electrical connections from panel to tub to make sure everything was tight
Removed control board cover (with power off) and check for any loose connections
Tested OHMS between lugs on element (read 13 - 13.5)
Removed wires going to lugs, turned on tub heat and the "Heat On" light comes on and seems to run normal

*Note* when looking at two lugs going into element it looks like they are covered with a lot of brown, rusty looking corrosion.

From the information, does it sound like I need a new element, electric assemble, or ????

Thanks you! Let me know if you require pictures or more information.


Offline
 Profile  
 
 Post subject:
PostPosted: Sun Feb 04, 2007 9:21 pm 

Joined: Fri Sep 03, 2004 12:27 am
Posts: 1153
Location: Albert Lea, MN
i think it's time for a new elemnet



_________________
Please be patient for replies

ATTENTION! USE THE ADVISE ON THIS FORUM WISELY! WE ARE NOT LIABLE FOR INJURIES, DEATH, DAMAGE, ETC. ARISING FROM THE USE OF THE INFORMATION IN THIS FORUM!

NOTE: I can't guarentee knowledge of all spas.
Offline
 Profile E-mail  
 
 Post subject:
PostPosted: Sun Feb 04, 2007 9:28 pm 

Joined: Sun Feb 04, 2007 1:23 pm
Posts: 11
Is http://spapartsnet.com/Electric-Heaters-Parts/Heater-Elements/55NINS_476_0_1.html the correct one? After reading the description of it Im still not sure to go with the 4500 or 5500.


Offline
 Profile  
 
 Post subject:
PostPosted: Mon Feb 05, 2007 1:34 am 

Joined: Fri Sep 03, 2004 12:27 am
Posts: 1153
Location: Albert Lea, MN
The smaller of the two will be better for the contactors that run it. The 5500 will heat faster, but will destroy your contactors faster. I always replace with the smaller... since the time it takes to heat isn't all that much slower. I'd rather not burn up components just to save a few minutes with the larger heater.



_________________
Please be patient for replies

ATTENTION! USE THE ADVISE ON THIS FORUM WISELY! WE ARE NOT LIABLE FOR INJURIES, DEATH, DAMAGE, ETC. ARISING FROM THE USE OF THE INFORMATION IN THIS FORUM!

NOTE: I can't guarentee knowledge of all spas.
Offline
 Profile E-mail  
 
 Post subject:
PostPosted: Mon Feb 05, 2007 9:43 am 

Joined: Sun Feb 04, 2007 1:23 pm
Posts: 11
Thanks charger, Ill be ordering one up today!


Offline
 Profile  
 
Display posts from previous:  Sort by  
 Page 1 of 1 [ 5 posts ] 

All times are UTC - 5 hours


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
AeroBlue: John Olson
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group