There are a few variables, however, first and foremost is the conduit depth. NEC is a minimum of 18" and many municipalities require it even deeper. Check with the local codes to be sure.
Second, depending on the type of wire, you can run up to 3 #6 wires in a 3/4" ridigid non-metallic tubing. That would be if it is THHN, THWN, or THWN-2. Notice there isn't "room" for a ground?
What I would do, and this is true in many spa cases, is tear out the 3/4", replace it with 1 1/4" (at proper depth), run 2 #6's for your hots, run a #8 for your neutral and a #8 for your ground. Most spas can get by with a smaller neutral since almost nothing runs at only 120V. Your pumps, heater, and blower are usually the 240V. The ground conductor can be one size smaller than your largest load lines, hence the #8.
That "electrician" that "walked off the job" could not have been a properly licensed electrician. I would be double checking everything that guy touched. Anyone in the industry knows you bury the rigid non metallic conduit at least 18" regardless what it is made of or it's size.