 Post subject: Seperate Disconnect Really needed?
PostPosted: Mon Jul 10, 2006 10:08 am 

Joined: Fri Jul 07, 2006 11:56 am
Posts: 12
Location: Denver
Ok, so I went to plan out the new 240 wiring for my hot tub and noticed code requires a seperate disconnect within 5 feet. Umm.. what if the main breaker box is within five feet.. then what?

Should I just use a 50AMP GFCI breaker in the main and not worry about a disconnect?

Thanks!

Rocky



_________________
"Mom, there's a fox in the hot tub!!"
Offline
 Profile  
 
 Post subject:
PostPosted: Mon Jul 10, 2006 1:58 pm 
Site Admin
User avatar

Joined: Tue Feb 03, 2004 11:39 am
Posts: 1406
Location: Metro Atlanta, Georgia Region
Definitely use a GFCI, however the requirement isn't that the cut-off must be within 5 feet, but GREATER THAN or Equal to 5 feet, and within sight of the spa. If your main is inside of 5 feet, it's not really safe because some day some drunk yo yo that wants to be a hero plays with the box while they're in the thing wet and all... I'm not referring to you :twisted: just covering all the possibilities.

Which is what the code tries to do.



_________________
Use this information at your own risk!
http://spapartsnet.com
http://atlanta.spanet.net
Amateurs built the Ark, Professionals built the Titanic.
Offline
 Profile E-mail  
 
 Post subject:
PostPosted: Wed Jul 12, 2006 12:19 am 

Joined: Fri Sep 03, 2004 12:27 am
Posts: 1153
Location: Albert Lea, MN
Pageup is correct, you can not, by code, have any disconnecting means (or any electrical disconnect for anything else) within 5' of the closest INSIDE edge of the spa. Not even a simple outlet! IMHO it should be 10 feet, considering people can have things in their hands that is conductive, but that is just me...

Regarding the additional disconnect, yes, you must have it. Why? The NEC doesn't specifically state why, but those in the know will tell you that the reason is because the main panel is a source for other circuits, and you can't guarentee that "Jo Blow" will know which breaker to throw in case of emergency.

I always recommend that the GFI breaker is located in the main panel, feeding the disconnect. A GFI placed only in the disconnect will leave the LINE side of the disconnect unprotected by a GFI and could still pose a risk at the disconnect. The code doesn't require my recommendation, it's just common sense.



_________________
Please be patient for replies

ATTENTION! USE THE ADVISE ON THIS FORUM WISELY! WE ARE NOT LIABLE FOR INJURIES, DEATH, DAMAGE, ETC. ARISING FROM THE USE OF THE INFORMATION IN THIS FORUM!

NOTE: I can't guarentee knowledge of all spas.
Offline
 Profile E-mail  
 
 Post subject:
PostPosted: Thu Jul 13, 2006 10:23 am 

Joined: Thu Jul 13, 2006 9:38 am
Posts: 5
Quote:
I always recommend that the GFI breaker is located in the main panel, feeding the disconnect..

Interesting... That's what I plan on doing, but was actually concerned that having the GFI in the service panel instead of the shutoff box was somehow wrong. You always see the "spa shutoff" boxes with the GFI breaker built-in, so I always assumed that was the way to go.

Here's a blurb I read on another site that seemed to indicate having it closer to the equipment is better...

Quote:
Why aren't all breakers and outlets GFCIs? The first answer is probably cost, for they cost two to four times as much as a standard one. Practical reason is that some appliances or circuits operate normally with slight variations in current, so the GFCI would constantly be breaking circuits for the wrong reason. In fact, slight variations might occur in the pool or spa equipment, causing the GFCI to trip even though everything is functioning properly. For this reason, it is best to locate the GFCI as close to the appliances as possible.

Is there a legitimate risk of the GFI tripping if it's too far away from the spa?


Offline
 Profile  
 
 Post subject:
PostPosted: Thu Jul 13, 2006 10:44 am 
Site Admin
User avatar

Joined: Tue Feb 03, 2004 11:39 am
Posts: 1406
Location: Metro Atlanta, Georgia Region
No.

And this is not a correct statement:
"circuits operate normally with slight variations in current, so the GFCI would constantly be breaking circuits for the wrong reason."

Along with the statement following it which is really full of crap.

A gfci doesn't trip because of current variation. it trips because of ground fault.

However, certain rf noise and other types of garbage electrons on the power lines can cause a some gfi's to falsely trip under ideal circumstances.

There's bazillions of gfci's mounted in main breaker boxes all over the country.

That said 1: it is easier to troubleshoot a ground fault related problem when the gfci is at the remote box.

That said 2: a gfci will last longer mounted in the house mains due to less exposure to the elements in an outside disconnect.

That said 3: as charger mentioned, if you accidentally cut into the spa power line with a mower or weed wacker, at least accidental shock risk is significantly reduced by having the gfci covering the line all the way to the spa/disconnect box.



_________________
Use this information at your own risk!
http://spapartsnet.com
http://atlanta.spanet.net
Amateurs built the Ark, Professionals built the Titanic.
Offline
 Profile E-mail  
 
 Post subject:
PostPosted: Thu Jul 13, 2006 12:07 pm 

Joined: Thu Jul 13, 2006 9:38 am
Posts: 5
Quote:
A gfci doesn't trip because of current variation. it trips because of ground fault...

Pageup, thanks for that explanation. This thread has cleared up some concerns for me and I feel a lot better about installing the GFI in my main load center. I'm working on resurrecting a late 1980s spa which has no GFI protection at all right now. Needless to say, nobody is getting near that thing until I get a GFI breaker installed!


Offline
 Profile  
 
 Post subject:
PostPosted: Fri Jul 14, 2006 7:25 pm 

Joined: Fri Jul 07, 2006 11:56 am
Posts: 12
Location: Denver
Hmm.. it appears as thought this Control (1995 Hurricane Products) has a GFCI built-in to the box. I'm assuming another GFCI is still required yes?

Rocky



_________________
"Mom, there's a fox in the hot tub!!"
Offline
 Profile  
 
 Post subject:
PostPosted: Fri Jul 14, 2006 7:36 pm 
Site Admin
User avatar

Joined: Tue Feb 03, 2004 11:39 am
Posts: 1406
Location: Metro Atlanta, Georgia Region
Don't ever trust built in GFCI's.

They are unreliable and when they fail, they usually fail with POWER ON. Not off.

Especially since that one's 11 years old.



_________________
Use this information at your own risk!
http://spapartsnet.com
http://atlanta.spanet.net
Amateurs built the Ark, Professionals built the Titanic.
Offline
 Profile E-mail  
 
Display posts from previous:  Sort by  
 Page 1 of 1 [ 8 posts ] 

All times are UTC - 5 hours


Who is online

Users browsing this forum: Yahoo [Bot] and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
cron
AeroBlue: John Olson
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group