 Post subject: Voltage in spa water
PostPosted: Wed Oct 04, 2006 9:41 pm 

Joined: Wed Aug 09, 2006 7:16 pm
Posts: 6
Location: MA
I have a spa that is a true 240 vac ,I have it wired to a 2 pole 30 amp gfci in a subpanel . The red(L1) goes to one load on the breaker and the black(L2) goes to the other load connection on the breaker. The load neutral of the breaker is vacant .The white pigtail on the breaker is attached to the insulated bus bar. The green ground coming from the spa is connected to the grounded bus in the subpanel. All is fine when the heater is not on ,but when the heater comes on there is 64 volts when I take measure from the spa water to the earth. If the heater is delivering the voltage why doesn't the breaker trip? How is the heater putting voltage to the water? The heater is heating the water. The spa is obviously not being used.Thanks, Chris


Offline
 Profile E-mail  
 
 Post subject:
PostPosted: Wed Oct 04, 2006 9:56 pm 
Site Admin
User avatar

Joined: Tue Feb 03, 2004 11:39 am
Posts: 1406
Location: Metro Atlanta, Georgia Region
Not enough info.

How old is the spa heater?
How old is the GFCI?

Have you taken a resistance reading between either leg of the heater element and ground? (With the power off of course).

Also, a DMM can pick up 64 volts right out of thin air given the right circumstances.



_________________
Use this information at your own risk!
http://spapartsnet.com
http://atlanta.spanet.net
Amateurs built the Ark, Professionals built the Titanic.
Offline
 Profile E-mail  
 
 Post subject:
PostPosted: Wed Oct 04, 2006 10:09 pm 

Joined: Wed Aug 09, 2006 7:16 pm
Posts: 6
Location: MA
The heater is in a sweewater austin 1999 . I found the problem by standing on the wet grass and touching the water when the heater was on. Not a nice surprise.
The breaker is a new Murray.
I have not taken any readings between the heater terminals yet.
Chris


Offline
 Profile E-mail  
 
 Post subject:
PostPosted: Wed Oct 04, 2006 10:14 pm 
Site Admin
User avatar

Joined: Tue Feb 03, 2004 11:39 am
Posts: 1406
Location: Metro Atlanta, Georgia Region
Do you have a 'Wiggy' style voltage tester that you can use? (Electro-mechanical meter).



_________________
Use this information at your own risk!
http://spapartsnet.com
http://atlanta.spanet.net
Amateurs built the Ark, Professionals built the Titanic.
Offline
 Profile E-mail  
 
 Post subject:
PostPosted: Wed Oct 04, 2006 10:24 pm 

Joined: Wed Aug 09, 2006 7:16 pm
Posts: 6
Location: MA
no, just digital.
I know the voltage is present because it shocked me.
Chris


Offline
 Profile E-mail  
 
 Post subject:
PostPosted: Wed Oct 04, 2006 10:45 pm 
Site Admin
User avatar

Joined: Tue Feb 03, 2004 11:39 am
Posts: 1406
Location: Metro Atlanta, Georgia Region
My first point in this is to go after the GFCI. (Fix heater is priority 2). Either it's not hooked up correctly (somehow?) or it's faulty. I have zero experience with Murray brand GFI's so right now I can trust yours about as far as I could throw it.

I was asking the question because that's the quickest (and safest) way to do an outside test on a GFCI, using a wiggy volt meter. One probe on any leg of the gfci (or either power lead at the control), and touch the other to ground - it should trip.

Of course this isn't a minimum current level test, but it'll at least give you an indication of operability with an outside imposed ground fault. If you have a reasonable appreciation of electrical safety, a 5 watt 4.7k resistor to ground is a good test too.

I take it the test button works on this gfci?
And you only have one circuit breaker going to this tub?



_________________
Use this information at your own risk!
http://spapartsnet.com
http://atlanta.spanet.net
Amateurs built the Ark, Professionals built the Titanic.
Offline
 Profile E-mail  
 
 Post subject:
PostPosted: Thu Oct 05, 2006 5:49 pm 

Joined: Wed Aug 09, 2006 7:16 pm
Posts: 6
Location: MA
This is what I have found, the last guy who worked on the spa replaced the heater and did not use the straps or any other method of grounding the heater. The heater had no connection to any bonding or grounding. The element must have failed introducing the voltage to the water. I attached a jumper from the heater case to a bonding lug on the spa panel and as soon as the heater fired the breaker tripped. This heater has no mounting studs and MUST be grounded.
Thanks, Chris


Offline
 Profile E-mail  
 
Display posts from previous:  Sort by  
 Page 1 of 1 [ 7 posts ] 

All times are UTC - 5 hours


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
AeroBlue: John Olson
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group