I am in the process of doing the pre-wiring for a LeisureBay spa. I've read over several forums and many mention running #6 wire however the electrician says I can use #8. I will be wiring into my main outside panel to a disconnect box 75ft away. The spa has two motors and a 4kw heater. Which wire should I use?
Thanks Rick
|
|
|
|
|
 |
|
jeffz
|
Post subject: Posted: Sun Jun 12, 2005 12:58 pm |
Joined: Thu Jun 09, 2005 2:51 pm Posts: 242 Location: Tucson, AZ
|
|
Hi, What will you total amp load be? What voltage, 208 or 240? What kind of wire, copper or aluminum?
_________________ Jeff
Servicing spas and hot-tubs can be DANGEROUS! If you do not know what you are doing, then please, do not attempt to use the information contained in this message, call a Spa Service Company to service your spa!
|
|
|
|
 |
|
Guest
|
Post subject: Posted: Sun Jun 12, 2005 1:21 pm |
|
|
|
240v using copper wire on a 50amp breaker in the main with a 50a GFCI in the disconnect box
|
|
|
|
|
 |
|
jeffz
|
Post subject: Posted: Sun Jun 12, 2005 1:34 pm |
Joined: Thu Jun 09, 2005 2:51 pm Posts: 242 Location: Tucson, AZ
|
|
240v, copper wire, 50-amp circuit, 75' run one way, #8 wire is the minimum and is within the National Electric Code (NEC). If you can fit it in the conduit, and the cost is reasonable, you could use the #6 wire, it is an extra insurance.