You didn't say if it was a 50 amp GFCI breaker, (a breaker with a little test button on it), so I'm assuming for now it's just standard.
You need to feel the circuit breaker for it's temperature when it's running, and/or after it trips. If it's excessively hot, then the problem is usually the screws that hold down the wires in the breaker are loose, there's corrosion setting in, or other things that will create resistance in the connection. This resistance creates the heat that will cause the breaker to trip.
If it's been doing it a lot, and the connection is the source of the problem, then most likely your breaker is heat damaged and you'll need to replace it as well as check the connecting wire for heat damage.
Here's some classic examples of this problem:
http://spasupport.com/electrical/main/burnedwires.html
Thanks and let us know how it turns out.