 Post subject: GFCI trips like clockwork - every 2 hours (exactly)
PostPosted: Sun Nov 19, 2006 8:58 pm 

Joined: Fri Nov 17, 2006 9:52 am
Posts: 3
I have a 1994 Caldera Spa connected to a 220V/50A
breaker w/GFCI in the house electrical panel.

With help from this forum I replaced the heater
2 weeks ago, and the spa ran well for two weeks.

However the GFCI has started tripping, and trips
EXACTLY 2 hours after I reset it. All systems
function perfectly during the 2 hour window
between a reset and the next trip.

Any suggestions on what I need to fix?


Offline
 Profile  
 
 Post subject:
PostPosted: Sun Nov 19, 2006 9:07 pm 
Site Admin
User avatar

Joined: Tue Feb 03, 2004 11:39 am
Posts: 1406
Location: Metro Atlanta, Georgia Region
Try it again.... at the point when the breaker trips, feel it to see if it's really warm. (So, you need to be waiting for it to happen).

If so, then your connections are loose at the gfi. You need to ascertain this first before moving forward with any other diagnostic.



_________________
Use this information at your own risk!
http://spapartsnet.com
http://atlanta.spanet.net
Amateurs built the Ark, Professionals built the Titanic.
Offline
 Profile E-mail  
 
 Post subject:
PostPosted: Mon Nov 20, 2006 9:21 am 

Joined: Fri Nov 17, 2006 9:52 am
Posts: 3
No, the breaker is not warm when the GFCI trips.
[Today it tripped with the heater turned off.]

What is the next most likely culprit for the regular
2 hour GFCI trip?


Offline
 Profile  
 
 Post subject:
PostPosted: Mon Nov 20, 2006 10:47 am 
User avatar

Joined: Sun Apr 03, 2005 12:50 am
Posts: 939
Location: SW Florida
Since it happens reguarily (every 2 hours) Page-up suggested an over-heating breaker (or over-heating wiring)- something not GFCI related, but FLA related. The breaker will trip for 2 reasons - too many amps (or burnt wires), or ~5 or more milli-amps of current leakage.

I think that's the best place to start- look for overheated wiring. If that's not it- I'd unplug the ozonenator, and it's always possible you hot a bad heater out of the box.

Other things- maybe something is getting wet, a slight drip getting where it shouldn't be- but Pageups course is the first place to look.

Do you have a meter that can test for current leakage (20m/10a)? It would make it a little easier to troubleshoot



_________________
t'was a woman that drove me to drink, and I've never had the courtesy to thank her
Offline
 Profile  
 
 Post subject:
PostPosted: Mon Nov 20, 2006 11:44 am 
Site Admin
User avatar

Joined: Tue Feb 03, 2004 11:39 am
Posts: 1406
Location: Metro Atlanta, Georgia Region
Thanks sw... I was going to say the same thing - if it really IS and exact 2 hour thing, then the ozonator is the first thing to unplug and see if it goes away.

The thing with temperature check is very important because if it's not caught early, one can end up with a fried gfci which is no fun (and $$$) to replace.



_________________
Use this information at your own risk!
http://spapartsnet.com
http://atlanta.spanet.net
Amateurs built the Ark, Professionals built the Titanic.
Offline
 Profile E-mail  
 
 Post subject: 2 hour tripping fixed
PostPosted: Mon Nov 27, 2006 10:10 am 

Joined: Fri Nov 17, 2006 9:52 am
Posts: 3
Many thanks to Pageup and Swine. The recurring
2 hour problem was the ozonator!


Offline
 Profile  
 
Display posts from previous:  Sort by  
 Page 1 of 1 [ 6 posts ] 

All times are UTC - 5 hours


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
AeroBlue: John Olson
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group