 Post subject: tiger Springs Manora Model M- GFCI trips after I turn Jets off
PostPosted: Mon Sep 17, 2007 1:34 pm 

Joined: Mon Sep 17, 2007 1:23 pm
Posts: 14
Location: portland, oregon
Hi:

I have a 1994 Tiger Springs Manora Model M ( serial #240050).

it's 115Volt, 20 amp ( on a dedicated 20amp grounded solo outlet )

I just purchased this spa ( 3rd owner ) and am having the following issue.

I filled the tub to the fill line ( 4-6 inches from the top, per the manual )

plugged in, tested the GFCI, per the manual and it works.

I turned the heater dial to 5, then pushed the button for "jets"... left it on for a few hours to run it.. the tub heated the water from a starting point of 70degrees F to a finishing point of 76F ( in about 3 hours ).. I turned the jets off and went to bed, assuming the water would still heat.

In the morning, the tub was cold again, and the heater not working.. It looked like the GFCI had tripped, so i reset and restarted the jets...

did this several times.. then realized that if I reset the GFCI and did not turn the jets on... it would trip after about 15-20 seconds.

It doesn't trip when the jets ( or light ) are running.. but as soon as I turn the jets off, the GFCI will trip and the heat will turn off.

I have the records that show the GFCI was replaced about 4 years ago.. just wondering if any of you pros have experienced this and have advice before I call for service.

Thank you,

Todd


Offline
 Profile  
 
 Post subject:
PostPosted: Mon Sep 17, 2007 1:47 pm 
Site Admin
User avatar

Joined: Tue Feb 03, 2004 11:39 am
Posts: 1406
Location: Metro Atlanta, Georgia Region
Unplug the heater from the control box and try the test again.

If it works, then you may have a faulty heater element causing the gfci to trip.

Then again, your gfci could be defective too.

I prefer to replace those cord based GFCI's with a standard 20 amp 115 volt plug, and install a 20 amp GFCI in the wall socket, or change the breaker in the house to a 20 amp GFCI.



_________________
Use this information at your own risk!
http://spapartsnet.com
http://atlanta.spanet.net
Amateurs built the Ark, Professionals built the Titanic.
Offline
 Profile E-mail  
 
 Post subject: Response-
PostPosted: Mon Sep 17, 2007 2:34 pm 

Joined: Mon Sep 17, 2007 1:23 pm
Posts: 14
Location: portland, oregon
Pageup- Thanks for the quick response.

I don't think I was clear enough. My cord is a 20am/115 v rated single plug ( no gfci inline ). I have a single outlet that the cord plugs into, and there is a 20amp GFCI circuit breaker in the panel.

I didn't see an electrical plug for the heater in the control panel.. I did see that the light plugs into the GFCI in the control panel, but that was the only one I saw. ... am I missing it?

thanks again for your help. It's very much appreciated.

todd


Offline
 Profile  
 
 Post subject:
PostPosted: Mon Sep 17, 2007 3:03 pm 
Site Admin
User avatar

Joined: Tue Feb 03, 2004 11:39 am
Posts: 1406
Location: Metro Atlanta, Georgia Region
Sorry, wrong make and year.

What I'd do is remove both wires that go to the heater element (tape up / be sure they don't touch anything) and see if that stops the tripping.

http://spapartsnet.com/Electric-Heaters ... 6_0_1.html



_________________
Use this information at your own risk!
http://spapartsnet.com
http://atlanta.spanet.net
Amateurs built the Ark, Professionals built the Titanic.
Offline
 Profile E-mail  
 
 Post subject: response
PostPosted: Mon Sep 17, 2007 4:23 pm 

Joined: Mon Sep 17, 2007 1:23 pm
Posts: 14
Location: portland, oregon
so if I remove the wires and breaker doesn't trip, I can assume the heater element needs to be replaced with the one you listed above?

thanks again,

Todd


Offline
 Profile  
 
 Post subject:
PostPosted: Mon Sep 17, 2007 8:40 pm 
Site Admin
User avatar

Joined: Tue Feb 03, 2004 11:39 am
Posts: 1406
Location: Metro Atlanta, Georgia Region
Yes.



_________________
Use this information at your own risk!
http://spapartsnet.com
http://atlanta.spanet.net
Amateurs built the Ark, Professionals built the Titanic.
Offline
 Profile E-mail  
 
 Post subject:
PostPosted: Tue Sep 18, 2007 3:20 pm 

Joined: Mon Sep 17, 2007 1:23 pm
Posts: 14
Location: portland, oregon
thanks for your help.

I'll be trying that this evening.

I'm really stumped though wtih this one.

This is supposed to be an either/or type of setup. either the jet pump or the heater should be on at one time, not both, since this is a 20 amp setup and the heater draws 12 amps alone( i think ).

seems to me that since the water is heating fine when the jets are running, but it shuts off when they're not, then maybe whoever wired it up, crossed some wires or something.

thoughts?

Thanks,


Offline
 Profile  
 
 Post subject:
PostPosted: Tue Sep 18, 2007 5:02 pm 
Site Admin
User avatar

Joined: Tue Feb 03, 2004 11:39 am
Posts: 1406
Location: Metro Atlanta, Georgia Region
Well you got your logic incorrect here...
Quote:
seems to me that since the water is heating fine when the jets are running


That's the thing, its NOT heating when the jets are on.

It turns the heater on when you turn the jets off, which trips the gfci.



_________________
Use this information at your own risk!
http://spapartsnet.com
http://atlanta.spanet.net
Amateurs built the Ark, Professionals built the Titanic.
Offline
 Profile E-mail  
 
 Post subject:
PostPosted: Tue Sep 18, 2007 7:09 pm 

Joined: Mon Sep 17, 2007 1:23 pm
Posts: 14
Location: portland, oregon
so if it's not heating when the jets are on.. how is the water getting hotter? ( about 2 degrees per hour when the jets are running.

see how this doesn't make sense?

When the jets are off.. the heater shuts off after about 20 seconds.


Offline
 Profile  
 
 Post subject:
PostPosted: Tue Sep 18, 2007 7:24 pm 
Site Admin
User avatar

Joined: Tue Feb 03, 2004 11:39 am
Posts: 1406
Location: Metro Atlanta, Georgia Region
Your pump is passively heating the water.

(Put your hand on it after it's been running for a while).



_________________
Use this information at your own risk!
http://spapartsnet.com
http://atlanta.spanet.net
Amateurs built the Ark, Professionals built the Titanic.
Offline
 Profile E-mail  
 
Display posts from previous:  Sort by  
 Page 1 of 3 [ 25 posts ]  Go to page 1, 2, 3  Next

All times are UTC - 5 hours


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
cron
AeroBlue: John Olson
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group