 Post subject: aqualine em-103 no element with pump on
PostPosted: Sun Aug 13, 2006 9:28 pm 

Joined: Sat Aug 12, 2006 2:39 pm
Posts: 4
i have an old aqualine em103. cat#26-2150. can heat tub to 104 in no time,when pump is just circulating. with pump on,hi or lo ,element turns off. any thoughts where 2 start. it is a 220volt pack


Offline
 Profile  
 
 Post subject:
PostPosted: Mon Aug 14, 2006 5:30 pm 

Joined: Fri Sep 03, 2004 12:27 am
Posts: 1153
Location: Albert Lea, MN
Sounds like it's working good



_________________
Please be patient for replies

ATTENTION! USE THE ADVISE ON THIS FORUM WISELY! WE ARE NOT LIABLE FOR INJURIES, DEATH, DAMAGE, ETC. ARISING FROM THE USE OF THE INFORMATION IN THIS FORUM!

NOTE: I can't guarentee knowledge of all spas.
Offline
 Profile E-mail  
 
 Post subject: No heat on high
PostPosted: Tue Aug 15, 2006 10:24 pm 

Joined: Tue Aug 15, 2006 9:18 pm
Posts: 133
Hi Torrezz,
If the system is set up for a 30 amp maximum load, the the controller
must disable the element to accomodate the amperage draw.
Element at 5.0 KW is roughly 25 amps.



_________________
Over 20,000 served
Offline
 Profile  
 
 Post subject:
PostPosted: Sun Aug 20, 2006 9:00 am 

Joined: Sat Aug 12, 2006 2:39 pm
Posts: 4
thanx for input hotwater. what if i'm on 50 amp,which i am


Offline
 Profile  
 
 Post subject: Won't Heat On High
PostPosted: Sun Aug 20, 2006 11:19 am 

Joined: Tue Aug 15, 2006 9:18 pm
Posts: 133
Hi Torrezz,

The Brett Aqualine heaters came in 110v operation setup, and 220v models.
If there is not a "conversion toggle switch" where you wire up the unit or an "amp plug" style pigtail to configure a 220v heater feed, then you may have a 110v unit.
At a glance, the 220v applications will have a "Contactor"
( http://spapartsnet.com/Electrical-Parts ... 6_1_1.html )
If you feed the heater line#2 of a 220v circuit instead of a neutral, then it will heat at a capacity of 5.5-6 KW. However, the componants involved such as the thermostat, high limit switch, and pressure switch, are not designed to carry the amperage of a 220v load. ( Most switches are 20 amp rated ) It will work, but you will start to wear out parts, and or see wire connections fail.

Above all of this, Safety is the concern.

There has to be a "Line Side GFCI" ( Ground Fault Circuit Interrupter ) with a 220v application. If you have an intergral 110v GFCI within the pack, it won't be sufficient.

This either helped, or confused the snot out of the situation. ( My head is spinning)
:roll:

Let me know



_________________
Over 20,000 served
Offline
 Profile  
 
 Post subject:
PostPosted: Mon Aug 21, 2006 4:50 pm 

Joined: Sat Aug 12, 2006 2:39 pm
Posts: 4
inhotwater, ok, your info did both. when we got tub home line #2 was on nuetral,industrial electrician from my plant said tub was wired wrong,he put #2 hot and nuetral,nuetral. tub was wired 220v from location it was moved.
guess more pertenant ? would be should element cook on all speeds as long as water temp has'nt met t-stat setting?
once again,thanx for sharing your knowledge/experience


Offline
 Profile  
 
 Post subject: Heater
PostPosted: Wed Aug 23, 2006 7:03 pm 

Joined: Tue Aug 15, 2006 9:18 pm
Posts: 133
:)



_________________
Over 20,000 served
Offline
 Profile  
 
Display posts from previous:  Sort by  
 Page 1 of 1 [ 7 posts ] 

All times are UTC - 5 hours


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
AeroBlue: John Olson
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group