 Post subject: Correct Kw Heater for 350gal hot tub
PostPosted: Sat Mar 19, 2005 8:59 pm 

Joined: Mon Jan 10, 2005 2:53 pm
Posts: 13
I have a 240v 350 gallon LA spa, it had a 5.5Kw heater and that would heat up the water 8-10deg/hr. I just put in a new heater element but it is only a 4.5Kw and I am only getting 2-4Deg/Hr. This does not make sense to me I expected it to heat at 5-8 deg/hr. I have checked the voltage supply during the heat cycle and I am seeing 120v at both inputs, after installation I checked the heater element and It had the correct resistance per the manual, I believe it was 14 ohms. Any one have any input or suggestions.

Thanks,

Fran


Offline
 Profile  
 
 Post subject:
PostPosted: Sun Mar 20, 2005 2:01 am 

Joined: Fri Jan 21, 2005 8:44 pm
Posts: 5
A 350 gallon tub has 1325 liters of water weighing 1,325,000 grams. A 14 Ohm resistor at 240V is a 4.1 KW heater. Supplying 14,810,400 Joules per hour which is 3,537,234 calories per hour ( 4.187 J/C). Your 350 gallons will take 736,111 calories to heat one degree Farenheit. Thus you should expect no more than 4.8 degrees F per hour heating. If you were a little off on the resistance measurement and the element really is 4.5KW, then the best you could expect is 5.2 degrees per hour. Your old heater would have done about 6.4 degrees per hour. It would take a 7 KW heater to heat at 8 degrees per hour. The calculations assume no loss (losses will slow heating) and no gains from motor power.


Offline
 Profile  
 
 Post subject:
PostPosted: Tue Apr 05, 2005 12:58 am 

Joined: Fri Sep 03, 2004 12:27 am
Posts: 1153
Location: Albert Lea, MN
check voltage at the element. Forgetting all that calorie/joules stuff... a 1.4KW heater will heat a 350 gallon tub with 110 power at about half the rate you are getting. A 220V 5K heater will do nearly 14 per hour. Those are real world figures from personal experiance with several tubs. I would check to see if you are getting full voltage AT THE HEATER ELEMENT. If you are, ensure you have the correct element (even if the seller told you it was a 4.5KW). Ensure you are well insulated, and the cover is on the tub during this time. Also make sure the blower isn't on and the air induction valves are closed.



_________________
Please be patient for replies

ATTENTION! USE THE ADVISE ON THIS FORUM WISELY! WE ARE NOT LIABLE FOR INJURIES, DEATH, DAMAGE, ETC. ARISING FROM THE USE OF THE INFORMATION IN THIS FORUM!

NOTE: I can't guarentee knowledge of all spas.
Offline
 Profile E-mail  
 
Display posts from previous:  Sort by  
 Page 1 of 1 [ 3 posts ] 

All times are UTC - 5 hours


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
cron
AeroBlue: John Olson
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group