Power at the coil (110 volts) needs a path. If you are reading across both coil terminals and getting 110 volts, then you should get the carriage to drop. If you picked up a 220 volt coil contactor, then it wouldn't energize. (just buzz) If you get zero accross the coil terminals, then you are missing line, or neutral.
So ...
forget T1, and L1 (loads) we've established that they are there.
Always read coil voltage from one side of the coil to the other. Never one side to ground.
110 volts across coil makes the world go round.
No voltage = no pressure switch completion. (funny looking round thing screwed into the 3"
verticle heater canister, or in the 2" flow through heater chamber.Older packs mounted the pressure switch to the back of the controller, and fed it with a brass hose barb, and lexan tubing.)
You also may have a capacitor across the coil set. It will be a green "chicklet" looking piece.
It's job is to soften the current to the coil, and reduce "chattering" that spikes other components.
If it were thrown out, no big deal.
Usually, Hurricane Products used orange to feed line from pressure switch, and of course, white for commons, and neutrals.